There is a difference in the wording of the 2005 code vs. the 2008 code. The 2005 code states that raceways must have the same physical characteristics. 2008 says they must have the same electrical characteristics.
Does anyone know why they changed the wording?
The reason for my question is this:
Can I run parallel feeders in different size conduits? I have a 3" GRC and a 2 1/2" GRC running in parallel that are already existing in the building feeding two panels side by side. I want to use them to feed a single 600A panel with 350MCM. Everything fits according to conduit fill. The conduits follow the exact same path and terminate in the MDP together.
Thanks for your input!
Chris
Does anyone know why they changed the wording?
The reason for my question is this:
Can I run parallel feeders in different size conduits? I have a 3" GRC and a 2 1/2" GRC running in parallel that are already existing in the building feeding two panels side by side. I want to use them to feed a single 600A panel with 350MCM. Everything fits according to conduit fill. The conduits follow the exact same path and terminate in the MDP together.
Thanks for your input!
Chris