S sharan Senior Member May 14, 2009 #1 Is there a limitation for the distance of secondary feeders from outdoor pad mounted transformer and main service disconnect in the building?
Is there a limitation for the distance of secondary feeders from outdoor pad mounted transformer and main service disconnect in the building?
A/A Fuel GTX Senior Member Location WI & AZ Occupation Electrician May 14, 2009 #2 That's a POCO issue and not covered in the NEC. They wouldn't be feeders but service entrance conductors.
That's a POCO issue and not covered in the NEC. They wouldn't be feeders but service entrance conductors.
iwire Moderator Staff member Location Massachusetts May 14, 2009 #3 No distance limitations for these service conductors under the NEC. If the NEC or NESC applies depends on where the service point is and that changes from area to area.
No distance limitations for these service conductors under the NEC. If the NEC or NESC applies depends on where the service point is and that changes from area to area.