Twoskinsoneman
Senior Member
- Location
- West Virginia, USA NEC: 2020
- Occupation
- Facility Senior Electrician
Just cut in a receptacle and use a cord....End of discussion.
The cord isn't subject to the same damage as the cable?
Just cut in a receptacle and use a cord....End of discussion.
The cord isn't subject to the same damage as the cable?
GET OUT OF MY HEAD!
I have been thinking about that very thing trying to justify it. But I do believe a cord to be OK and NM to be subject to damage.
That's a weird opinion but since it is open to interpretation I certainly wouldn't argue it. I'll just give my opinion that I disagree and personally don't see a case where NM would be subject to damage but not the cord
what the heck are these people doing under their sink to inflict all this damage on the nm ?
Ok I never thought of subject to damage as involving movement. So that may be indicated if there is no other rule involving movement after installation...A cord is much more tolerant to repeated bending at the connector then solid NM, at least IMO.
:grin:
If I was only really connected to them.![]()
Which method is $$$ saving for an electrical branch circuit installation to a disposer? Putting in a receptacle under the sink and having the plumber supply the pigtailed disposer later or having to come back and wire up the disposer with flex? Just thought I'd ask. rbj
Which method is $$$ saving for an electrical branch circuit installation to a disposer? Putting in a receptacle under the sink and having the plumber supply the pigtailed disposer later or having to come back and wire up the disposer with flex? Just thought I'd ask. rbj
I had always installed the recept., b/c it seemed to be less hassle that way. Less hassle means less $$$. We could usually get the duplex and plate installed before the sink was set into the hole. In some jurisdictions, we would install the dishwasher circuit on the other side of the same duplex recept. and put a two pole brkr in the panel.
We use a 4-square flush with the face of the studs, then a 1-1/2 extension and a duplex industrial cover. Wire it up and never touch it again. The cabinet guys cut the hole, slide the cab in and we never crawl in the cab at all. Plus, they never cover the darn plugs that way!
We use a 4-square flush with the face of the studs, then a 1-1/2 extension and a duplex industrial cover. Wire it up and never touch it again. The cabinet guys cut the hole, slide the cab in and we never crawl in the cab at all. Plus, they never cover the darn plugs that way!
How about we just agree to install all wiring under a sink in 1/2" rigid encased in 2" of concrete!![]()
Never thought of split-wiring one duplex?I have always just put two receptacles in two seperate single gang boxes under the sink. One for the dishwasher and one for the disposal.
Never thought of split-wiring one duplex?