I have a new industrial installation fed from a 13.8kv breaker at the utility substation. From here the 13.8kv runs overhead to a 13.8kv-480v unit substation. From the unit sub there are feeds to Motor control centers in several different buildings within the plant. The inspector is requiring service rated disconnects at each of these buildings, in front of the MCC incoming section.
My opinion is the point of service is at the 13.8kv breaker at the utility sub. The runs to the plant buildings are feeders and therefore do not require service rated disconnects.
Any opinions?
My opinion is the point of service is at the 13.8kv breaker at the utility sub. The runs to the plant buildings are feeders and therefore do not require service rated disconnects.
Any opinions?