MV Cable Quetsion
triniboy
Guys
Can someone tell me if when an MV Shielded MC cable is terminated are the shield foils brought out and tied to ground at both switchgear and transformer/motor or are they only tied down on one end i.e. the switchgear end.
Also does the NEC allow a MV MC cable to be terminated in a transformer termination box without using a gland as long as the interlocked armour is grounded at both ends.
Advice on these two points would be gratefully accepted.
Guys
1./ Can someone tell me if when an MV Shielded MC cable is terminated are the shield foils brought out and tied to ground at both switchgear and transformer/motor or are they only tied down on one end i.e. the switchgear end.
2./ Also does the NEC allow a MV MC cable to be terminated in a transformer termination box without using a gland as long as the interlocked armour is grounded at both ends.
1./ Both ends.
2./ The method of entry should be by a means that is designed and aprpoved for the purpose. Grounding the MC sheeting falls under the general philosphy of the NEC - basically - anything that houses, contains, routes electrical material to be bonded to grounding.