Hi All,
I am working on the design of a substation and there is a dispute about the working clearance requirement of our main switchgear. The line side switchgear (34.5kV) and the load side switchgear (13.8kV) are face to face in the electrical room.
Here are the two thoughts.
Camp 1 says this is a condition 1 clearance since the bus work can not be accessed from the front and when the circuit breaker is removed a barrier drops down to inhibit access to the buss. (See condition 1 statement after the or)
Camp 2 says that this is a condition 3 situation because you have live parts on both sides.
I've looked in the NEC handbook and while there is no explanation for NEC 110-34(A) there is an explanation for 110-26(A)(1). The problem is, the explanation for 110-26(A)(1) does not seem to address the exposed live parts on both sides that are effectively guarded by a barrier (Condition 1) scenario.
What does everyone think and can anyone direct me to a better explanation of which (and why) condition would apply.
Thanks in advance for your help,
Scott