Sometimes when we read the NEC, it is difficult to understand just what the wording actually means. I believe the section requiring the disconnecting means for generators is one of those. 445.18
Here is a clip I took from a CSE magazine article, by Michael Kirchner, Sales Training Manager, Generac Power Systems - 4.1.09
"
Is a disconnect required on the generator? NEC 445.18 shows a preference for the generator to be equipped with a disconnecting means but allows the disconnect?typically the generator breaker?to be removed, provided that the generator can be readily shut down and that it does not operate in parallel. So, even though the NEC allows the generator to be provided without an output breaker, standard industry practice is to include this disconnect.
Is another disconnect required at the point of building entrance, in addition to the generator breaker? The market implementation of this requirement seems to be split?half of the market requires an additional disconnect and half of the market does not. Because the cabling from the generator is a feeder, NEC 225.31 requires a disconnect at the point of building entry unless exempted in another part of the code. Enter the local interpretation of the requirements for an outdoor-housed generator set?NEC 700.12(B)(6), 701.11(B)(5), and 702.11?which state: ?When an outdoor housed generator set is equipped with a readily accessible disconnect means located within sight of the building or structure supplied, an additional disconnecting means shall not be required.?
The issue here is what needs to be visible from the building. If your answer is the generator, then an additional disconnect generally isn?t required. But if the answer is the generator disconnect, then an additional disconnect typically be required (most generator breakers are not visible from the building)."