Flex
 - poestenkill ny
I have two different lighting circuits in one 4 gang box. Each is feed from its own separate mc. Are the grounds required to be terminated together? I found 250.144 but am not sure if thats what it says.
they have to be right? Cause each circuit has to be bonded to the box anyway so might as well tie them all together. 2 electricians told me today to keep them seperate. I dont believe them.
also would like a code reference please
So they do need to be tied together
what if they are EGCs from different panels?
but what happens to the 1/0 rule on parallel installations? same length, and all that stuff?
310.4(A) General. Aluminum, copper-clad aluminum, or copper
conductors of size 1/0 AWG and larger, comprising each
phase, polarity, neutral, or grounded circuit conductor shall
be permitted to be connected in parallel (electrically joined
at both ends).
310.4(E) Equipment Grounding Conductors. Where parallel
equipment grounding conductors are used, they shall be
sized in accordance with 250.122. Sectioned equipment
grounding conductors smaller than 1/0 AWG shall be permitted
in multiconductor cables in accordance with 310.13,
provided the combined circular mil area in each cable complies
with 250.122.
250.122(C) Multiple Circuits.
Where a single equipment grounding
conductor is run with multiple circuits in the same
raceway, cable, or cable tray, it shall be sized for the largest
overcurrent device protecting conductors in the raceway,
cable, or cable tray. Equipment grounding conductors installed
in cable trays shall meet the minimum requirements
of 392.3(B)(1)(c).
310.4(A)does not initially apply to EGC's of individual circuits
Remove "initially" and "of individual circuits" and you've got it. :smile:
Roger
Ground is ground they are all common.