Somebody was not reading their NEC.
300.3 (B) 1
300.3 (B) 1

Last edited:
I don't have my code book. But I am guessing it has some thing to do with smooth surfaces and plastic bushings.
I don't have my code book. But I am guessing it has some thing to do with smooth surfaces and plastic bushings.
Wow. :roll:Nice handle tie
![]()
Wow. :roll:
Which side of the metering is the hot metal?
If it is on th supply side they are steeling electricity to heat the building. :wink:
Parallel conductors not routed together through a ferrous metal barrier. All they had to do was slot the barrier. Though I would have cut a 8" X 36 in hole and utilized insulaliner.
300.20(B) Individual Conductors. Where a single conductor
carrying alternating current passes through metal with magnetic
properties, the inductive effect shall be minimized by
(1) cutting slots in the metal between the individual holes
through which the individual conductors pass or (2) passing
all the conductors in the circuit through an insulating wall
sufficiently large for all of the conductors of the circuit.
Brian,
Do you have idea of the current level when the picture was taken?
The reason I asked is because it is my understanding that the equivalent to 300.20 in the Canadian Electrical code only applies to circuits that exceed 200 amps. Based on the number of conductors this was designed for a lot more than 200 amps, but the hot spot is only an 112 or so. I would expect that the current was a lot less than design load.I pulled the Discrepancy Report and the tech did not record the amperage. An over sight on his part.
Me, too, please? IM sent.This was a 1200 amp service.
Tom if you want a better digital copy IM me.