There is a new store going into a existing building. They have completely remodeled the building. They had an existing 4000 amp service that covered the new connected load of 2600 amps. So they left the main swithgear alone and went from there. They finished the store and I passed the final inspection. Now they have decided to add a transfer switch for a portable generator. From the transformer they pulled new conductors. They were 4 750 kcms good for 1900 amps. The transfer switch which is now the main service disconnect has a 2500 amp adjustable trip breaker. They, the engineers, said that the store will never reach the connected load and they sent me loads for "similar" stores. I said sorry no way. You must meet the connected load of the store. So they have an energy management system that they say they can use to change the load. They have sent me new drawings with the adjusted load using the ems and it is 2297 amps. They are going to install another 750 to get to 2375 and then they are going to dial down their breaker to 2300 amps. What are the issues to consider here? Should I allow the changed load with the ems used? Should the store be formally informed of the new load? Another issue is that there are no more conduits to the transformer, so they will have to cut the concrete between the transformer and the transfer switch and add a conduit for the extra 750. Thoughts?