LRB
Member
- Location
- Interior Alaska
For the grounding of the portable 200 KW Cat Gen set we are installing, Cat makes the following statement:
?In any generator installation, the frame of the generator must be positively connected to an earth ground. This connection is the first one that is made at the installation. This connection is the last one that should be removed ?
They discuss the need for this conductor to be flexible, and then they say that this cable or strap should have at least the current carrying capacity of the largest line lead to the connected load
Why does Cat require such a large grounding conductor tied to the frame of the gen? My GE will be a near by well casing. Is this grounding conductor between the gen frame and the well casing a GE jumper and gen frame part of the GES? What size of conductor do I need to satisfy Cat?s requirement? If the gen frame is part of the GES then my GEC will be a short jumper of 1/0 from gen T0 to the gen frame.
There is a 200 A 1-phase service to the facility that has a single ground rod for GE. The portable gen will be the sole source of power for the 480 V 3 phase. My understanding that the generator is a SDS and I will have to bond the 2 GE together to make one GES. Do I bond from GE to GE or from 1-phase service entrance to gen T0 or gen frame or the well casing? What size conductor for bonding jumper
?In any generator installation, the frame of the generator must be positively connected to an earth ground. This connection is the first one that is made at the installation. This connection is the last one that should be removed ?
They discuss the need for this conductor to be flexible, and then they say that this cable or strap should have at least the current carrying capacity of the largest line lead to the connected load
Why does Cat require such a large grounding conductor tied to the frame of the gen? My GE will be a near by well casing. Is this grounding conductor between the gen frame and the well casing a GE jumper and gen frame part of the GES? What size of conductor do I need to satisfy Cat?s requirement? If the gen frame is part of the GES then my GEC will be a short jumper of 1/0 from gen T0 to the gen frame.
There is a 200 A 1-phase service to the facility that has a single ground rod for GE. The portable gen will be the sole source of power for the 480 V 3 phase. My understanding that the generator is a SDS and I will have to bond the 2 GE together to make one GES. Do I bond from GE to GE or from 1-phase service entrance to gen T0 or gen frame or the well casing? What size conductor for bonding jumper