In n.y.c. Do I need to install a green tail from the receptacle to the steel drywall box???
E eelelectric New member May 19, 2009 #1 In n.y.c. Do I need to install a green tail from the receptacle to the steel drywall box???
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician May 20, 2009 #2 The answer is yes, unless you're using a self grounding receptacle in a box that is already properly grounded, then no tail is required. The NYC electrical code is based on the 2005 NEC and has almost no modifications of NEC article 250. Welcome to the forum. :smile:
K8MHZ Senior Member Location Michigan. It's a beautiful peninsula, I've looked Occupation Electrician May 20, 2009 #3 Could it be bare?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician May 20, 2009 #4 K8MHZ said: Could it be bare? Click to expand... You're right, I missed the part about it being green. It could also be bare.
V vinster888 Senior Member Location Nature Coast of Florida May 20, 2009 #5 the best part is when there is no egc and the box is loose. i love those