I just returned from a service call at a body shop where they are having problems with breakers tripping when thier resistance welder is in use. Im not too familiar with welders, and after reading through 630.31 I want to make sure Im not overlooking anything.
Here is the nameplate data on the welder:
Duty Cycle Capacity 50% - 24kVa
Voltage - 208V, 50/60Hz, 3 phase
Max Output - 6200A DC
Max Input - 74 kVa
Duty Cycle - 5.6%
The welder has a 50A cord/plug and there are 5 locations with 14-50R outlets available for use. 3 of the 5 outlets are on thier own breakers, the other two share one breaker. All the breakers are 50/3P and the supply conductors are all 8 awg.
Using 630.31A(2) using a value of 7.5% I get 55.5A and 5% is 45A - I assume I could extrapolate an exact current, but 50A seems about right.
The customer says the breaker trips after about 4 welds or so. I'm not sure the duration of the welds, or how that correlates to the duty cycle - but does this look like it would be fixed by increasing the OCP size? If so, is there a rule of thumb for sizing (50 -> 150)?
PART II
The customer also noted that a couple 20/1P breakers trip along with the welder on occasion that are located in a completely different panel. After opening the panel with the welder breakers in it, things became a bit odd.
The panel is a 200A MCP, that is fed with #1 AWG conductors that go to a tap can right below the panel and tap to some 500MCM that go to a 400A/3P breaker in the main switchboard. Both the ground and neutral land on a isolated bar in the panel, with both neutral and ground branch circuit wires landed on it.
Any idea why the breakers in the other panel would be tripping? If I increased the breaker size on the welding circuits (to prevent future trips), would I be leaving or strengthening a hazard?
I hope this makes sense, and any help is appreciated. Please let me know if more information is needed.
Max Input - 74 kVa
Duty Cycle - 5.6%
PART II