How serious is it?

Status
Not open for further replies.

smallfish

Senior Member
Location
Detroit
How serious is it not to have bonded to the enclosure, emt stubbing up out of the floor into an open-bottom main distribution panel?
There are four four-inch emt pipes with set screw connectors and couplings, each enclosing a parallel set of 750 kcmil aluminum feeders, each including an equipment bonding jumper sized appropriately and each jumper is terminated to a lug on the panel frame. The other end of the emt is connected to the metal frame of the switchgear by means of an emt connector. The pipe run is over a hundred feet.
Thanks
 

mikeames

Senior Member
Location
Germantown MD
Occupation
Teacher - Master Electrician - 2017 NEC
The risk is the insulation of the wire breaking down, shorting out to the EMT and not clearing the fault. Since the EMT is most likely grounded (but not well) its possible that a short would seriously heat the emt until it clears either through a breaker tripping or the conduit melting.
 