ericsherman37
Senior Member
- Location
- Oregon Coast
So, being an apprentice, I am still in the process of grasping some of the more basic concepts of electrical installations. That being said, I'll soon be helping with a project involving the installation of a transfer switch and generator for a small city Water Treatment plant. I helped haul down some parts and materials today, and my journeyman gave me a brief walkthrough of what we were going to be doing. It raised a few questions in my mind that I would like to receive input on, if y'all would be so kind 
Following is a picture of what we will tentatively be doing. There is no currently no transfer switch, just an MCC which contains pretty much everything the plant runs from. As is, the service (red wires) comes from underground right into the PoCo CT Metering cabinet, and then up over to the 600A service breaker. We will install the transfer switch immediately adjacent to the MCC.
As the caption states, the service breaker's load side is tied directly to the MCC bussing (busing?) with some jumper bars. My journeyman said we are going to remove these and run wires straight from the service breaker's load side over to the transfer switch (blue). The transfer switch load wires will come right back (purple) and land on some bus lugs which we will install at the location where we removed the bus jumper bars. A big switch loop, kind of.
Here's the picture I made, as I envision how this would work. A couple of questions follow:
1) With the blue set of wires coming from the service breaker load side, would a neutral need to be run with those phase wires? Intuition tells me so, but the transfer switch is a 3-pole and doesn't switch the neutral... it wouldn't be necessary for functionality, but something is telling me that it should be there. Or can it just stay where it originally is, landed on the MCC neutral bus?
2) I'm kind of confused about the generator EGC. It won't be a separately derived system, so the EGC isn't bonded to the generator neutral at its breaker enclosure. So if there was a fault to ground in, say, the generator conduit while the generator was running, am I correct in observing that the fault current would have to go allll the way back to the MCC ground bus, through the main bonding jumper and alllllllll the way back to the source via the generator neutral?
3) For that matter, how does the transfer switch go about getting bonded? Is a bonding jumper over to the MCC ground bus sufficient, as per the illustration? If so, would it be sized as an EGC based on the generator OCPD? Or the service OCPD? Or whichever is largest? Or would it be sized based on Table 250.66? Why?
4) Keep in mind that this illustration is based on a very quick glance at the setup and scenario. I haven't gotten to poke around at all so there may be some inaccuracies in the picture that don't reflect the actual setup. I am of course not running this job, but I haven't really had a chance thus far in my career to be involved in a backup system installation from the onset, so my curiosity is piqued and I'm just trying to understand the system. Therefore, the final question is: are there any glaring errors that I have overlooked? Anything to note? What did I miss or screw up on (aside from the previous questions).
Sorry for the really long post, but I greatly appreciate the time that anyone is willing to take to help me understand these concepts. Thanks!
P.S. PoCo approved and is fine with having the wiring run through their CT cabinet.
Following is a picture of what we will tentatively be doing. There is no currently no transfer switch, just an MCC which contains pretty much everything the plant runs from. As is, the service (red wires) comes from underground right into the PoCo CT Metering cabinet, and then up over to the 600A service breaker. We will install the transfer switch immediately adjacent to the MCC.
As the caption states, the service breaker's load side is tied directly to the MCC bussing (busing?) with some jumper bars. My journeyman said we are going to remove these and run wires straight from the service breaker's load side over to the transfer switch (blue). The transfer switch load wires will come right back (purple) and land on some bus lugs which we will install at the location where we removed the bus jumper bars. A big switch loop, kind of.
Here's the picture I made, as I envision how this would work. A couple of questions follow:

1) With the blue set of wires coming from the service breaker load side, would a neutral need to be run with those phase wires? Intuition tells me so, but the transfer switch is a 3-pole and doesn't switch the neutral... it wouldn't be necessary for functionality, but something is telling me that it should be there. Or can it just stay where it originally is, landed on the MCC neutral bus?
2) I'm kind of confused about the generator EGC. It won't be a separately derived system, so the EGC isn't bonded to the generator neutral at its breaker enclosure. So if there was a fault to ground in, say, the generator conduit while the generator was running, am I correct in observing that the fault current would have to go allll the way back to the MCC ground bus, through the main bonding jumper and alllllllll the way back to the source via the generator neutral?
3) For that matter, how does the transfer switch go about getting bonded? Is a bonding jumper over to the MCC ground bus sufficient, as per the illustration? If so, would it be sized as an EGC based on the generator OCPD? Or the service OCPD? Or whichever is largest? Or would it be sized based on Table 250.66? Why?
4) Keep in mind that this illustration is based on a very quick glance at the setup and scenario. I haven't gotten to poke around at all so there may be some inaccuracies in the picture that don't reflect the actual setup. I am of course not running this job, but I haven't really had a chance thus far in my career to be involved in a backup system installation from the onset, so my curiosity is piqued and I'm just trying to understand the system. Therefore, the final question is: are there any glaring errors that I have overlooked? Anything to note? What did I miss or screw up on (aside from the previous questions).
Sorry for the really long post, but I greatly appreciate the time that anyone is willing to take to help me understand these concepts. Thanks!
P.S. PoCo approved and is fine with having the wiring run through their CT cabinet.
Last edited: