I have a 480V 3phase ckt feeding a 20hp AHU with a VFD. Both the panel and the AHU are in the same mechanical room. On my drawing, I show a non-fused disconnect feeding the VFD so that there is a local disconnect available. Contractor comes back and says the VFD they purchased has an integral disconnect, so that is covered.
My question is: should i have placed a fused disconnect in front of the VFD instead of non-fused? My concern is fault current protection. I know some of these VFD's I've seen have only a 5kAIC rating.
I know we do the fault current calculations to provide panels and breakers with adequate AIC ratings....but what about end devices and their AIC ratings? They require protection too?
My question is: should i have placed a fused disconnect in front of the VFD instead of non-fused? My concern is fault current protection. I know some of these VFD's I've seen have only a 5kAIC rating.
I know we do the fault current calculations to provide panels and breakers with adequate AIC ratings....but what about end devices and their AIC ratings? They require protection too?