- Bremerton, Washington
- Master Electrician
There is an outside 450 KW generator mounted on an 860 gallon fuel tank. This puts the control panel and EPO 8 ft from grade. Whats needed is a platform all around the generator.
The generator main breaker is 7' 4" above grade to the center of the handle in the on postion. While the main breaker height violates 240.24(A), what is unclear is the EPO (emergency power off) and the control panel.
Section 445 per the following:
445.18 Disconnecting Means Required for Generators.
Generators shall be equipped with disconnect(s), lockable in the open position, by means of which the generator and all protective devices and control apparatus are able to be disconnected entirely from the circuits supplied by the generator except where both of the following conditions apply:
(1) The driving means for the generator can be readily shut down.
(2) The generator is not arranged to operate in parallel with another generator or other source of voltage.
(1) Refers to the EPO. What is "readily"? IMO, 8ft from grade is not readily.
There is also some language in NFPA 110 but its a bit unclear.
Am I missing anything?