A friend sent me an email asking why a dp breaker rated 120/277 cannot be used for 240 Volts. I have never noticed a breaker rated that way. Any help.
My first though would be to refer him to the "eyeglasses at Wal-Mart" thread![]()
If it was actually marked that way, there is no reason why you can't use it on a 120/240 volt system. The first number is the maximum permitted voltage to ground and the second is the maximum permitted phase to phase voltage. You could not use it on a 3 wire 240 volt system because of the 120 volt part of the "slash" rating.A friend sent me an email asking why a dp breaker rated 120/277 cannot be used for 240 Volts. I have never noticed a breaker rated that way. Any help.