Signal (4-20mA) with network cable

Status
Not open for further replies.
Network cable

Network cable

Network should be wired on a separate conduit.
Analog signal cables should be wired with shielded pairs, grounded at one end.
 
Network should be wired on a separate conduit.

Why? TP Ethernet is a transformer-isolated balanced signal, and current loop interfaces also tend to be balanced, at least as far as the sensor is concerned. They also IME tend to be very low speed (data-wise) and noise-insensitive, which is why you use them. Also IME they're usually wired with shielded cable, anyway.
 
The industry standard for separation of different voltage levels and signal types of electrical cable is API 552. I've attached a table out of API 552 with the recommended separation distances. Notice that these distances are based on five different levels of signals. Signals of the same level do not require separation, and it appears that ethernet and 4-20 mA signals are both level 2: DC signals under 28V.
 

Attachments

  • API 552 Table.JPG
    API 552 Table.JPG
    73.1 KB · Views: 11
Thanks for the table. I guess I will run my signal+network+24VDC control, and 24VDC power in the same conduit.
 
Thanks for the table. I guess I will run my signal+network+24VDC control, and 24VDC power in the same conduit.
 