What about 3?

Status
Not open for further replies.

lmchenry

Senior Member
334.80 states that where more than two NM cables...the allowable ampacity of each conductor shall be adjusted in accordance with 310.15B2a. 310.15B2a is for more than three current carrying conductors. So what about exactly three conductors? How are they rated?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Three conductors do not require derating, but how do you have only 3 current carrying conductors with more than on NM cable?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Are you refering to the neutral conductor as a current carrying conductor?

The neutral of a 2 wire circuit is a current carrying conductor. Take a look at 310.15(B)(4) for the conditions when a neutral conductor need not be counted as a current carrying conductor.

Chris
 

lmchenry

Senior Member
Yes, of course. But why does 334.80 say two NM containing two or more if it will always have 4 or more?
 

lmchenry

Senior Member
Thanks for getting my mind set correct. Also, wouldn't 2 NMs bundled be 4 current carrying conductors and by 310.15b2a need to be derated? Or does 334.80 override this? Straighten me out again.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Here's what it says:

334.80 Ampacity.
Where more than two NM cables containing two or more current-carrying conductors are installed, without maintaining spacing between the cables, through the same opening in wood framing that is to be fire- or draft-stopped using thermal insulation, caulk, or sealing foam, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(B)(2)(a) and the provisions of 310.15(A)(2), Exception, shall not apply.

Under normal circumstances if the bundling is 24" or less than derating will not apply. In this instance, even though the conductors are only bundled for about 3", derating does apply.
 

lmchenry

Senior Member
So how many contractors or inspectors derate 2 NMs that are under the same staples that run the length of a stud according to 310.15b2a?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
... wouldn't 2 NMs bundled be 4 current carrying conductors ...
Not in every case case, such as using two 2-cond NM's between a pair of 3-ways as hot and neutral as well as a pair of travelers. Besides, not all conductors carry their ampacities.

For example, there could be a 14-2 cable feed down to a 3-gang box and three 14-2's coming back up to hit three fixtures. The most the entire bundle would ever carry is 15a.

Then, you could have four 14-2's as home runs supplying four different circuits. Obviously, each cable could conceivably be loaded to its ampacity, making 60a for the same bundle.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
For example, there could be a 14-2 cable feed down to a 3-gang box and three 14-2's coming back up to hit three fixtures. The most the entire bundle would ever carry is 15a.

Are you saying this configuration would not require derating if bundled more then 24"?
 

kbsparky

Senior Member
Location
Delmarva, USA
Why is everybody afraid to derate some romex? Derate it already!!

Take (4) 14/2 NM cables, stuff `em into a hole, foam it up, and derate:

(8) conductors total
Table 310.15(B)(2) = 70%

Table 310.16 #14 rated at 25 Amps 90 degree column

Derated value = 17.5 Amps.

Limit circuit to 15 Amps per 240.4(D).

End result? NO CHANGE IN VALUE

So what's the big deal here?

Do the same with some #12's and you end up with 21 Amps, again limited to 20 Amp breaker. Still no change!

Edit to add: Just don't try this with your A/C circuit :rolleyes:
 