I have a situation where 4 parallel sets of 4" emt conduits, each enclosing an equipment grounding conductor and their circuit conductors, stub up into an open-bottom 1600 amp 480/277volt panelboard. Each equipment grounding conductor is lugged to the panelboard frame and is bonded back at the source enclosure switchgear. The four conduits originating at the switchgear are bonded to it by means of set screw emt connectors each in their own punched hole. Do the stubbed-up ends of the conduits require bonding to the panelboard enclosure?
If these raceways are not bonded to the panelboard to which the equipment grounding conductors are, and a fault occured in a raceway, would the fault path be back to the source solely through the one faulted raceway? Would the fault current carried by the other paralleled circuit conductors of the same faulting phase (from the source to the panelboard and back, in the other direction, to the fault) be impeded? Would the equipment grounding conductors carry any of the fault current?
It would seem that 05NEC Sections 300.10, 250.96 and 250.97 would require raceway bonding to panelboard.
Thank You
If these raceways are not bonded to the panelboard to which the equipment grounding conductors are, and a fault occured in a raceway, would the fault path be back to the source solely through the one faulted raceway? Would the fault current carried by the other paralleled circuit conductors of the same faulting phase (from the source to the panelboard and back, in the other direction, to the fault) be impeded? Would the equipment grounding conductors carry any of the fault current?
It would seem that 05NEC Sections 300.10, 250.96 and 250.97 would require raceway bonding to panelboard.
Thank You