i have a 50 hp 480 volt 65 or 75 fla wye/delta 2 speed motor for a commercial dough mixer . The mixer supposed to run 30 seconds in low speed ,then 30 seconds in high speed . We ran #3s thhn from the hv ge panel to feed the mcc. Every time the motor kicks into high speed the breaker trips . Im assuming there is a huge inrush of current in high speed . The motor guy said the windings were fine . Im pretty sure the contols and starters are fine because i disconnected the load from the starter and everything was working fine. Me and my partner are racking our brains for 4 months trying to figure this out. We now think we need a breaker that allows a large inrush of current at 2nd speed like a inverse time cb or an instantaneous trip breaker or just a bigger breaker period .We have a 100 amp ge breaker on there now , feeding the motor with #3s , the lenght of the run is approx. 170 feet . If i need a special breaker , should i increase the wire size, and the the breaker need a special enclosure if it doesnt fit in ge 600 amp panel . Can i get a breaker that is adjustable . I read in the code book about 800% to 1100% inrush current on certain breaker applications. Can you possibly help me my address is ginogag@optonline.net thanks