are light whips allowed in hospital patient rooms in fixtures above 7.5 feet
if the whip i am using is aluminum and using ul listed connectors approved for grounding is it ok if so how do i prove it and how can i prove rwa flex conduit is not mc
250.118(5) Listed flexible metal conduit meeting all the following conditions:
a. The conduit is terminated in listed fittings.
b. The circuit conductors contained in the conduit are protected by overcurrent devices rated at 20 amperes or less.
c. The combined length of flexible metal conduit and flexible metallic tubing and liquidtight flexible metal conduit in the same ground return path does not exceed 1.8 m (6 ft).
d. Where used to connect equipment where flexibility is necessary after installation, an equipment grounding conductor shall be installed.
As long as the sheath is recognized as an EGC in 250.118, see 517.13(B) Ex No 2.
Roger
Greg,
I'm not in disagreement, but I was addressing his Post #3. My post was partly generated by incidents where E/C's have installed "pre-assembled"
whips purchased from a third party. In those cases we have normally asked for the UL: (NRTL) listing of the assembly.
The use of a UL listed connector an a "purchased assembled whip" is not normally sufficient to inspectors in this area.