GFCI minimum trip rating

Status
Not open for further replies.

SiddMartin

Senior Member
Location
PA
Does anyone know the minimum trip rating for personal protection on a GFCI? Is there a different min. trip rating for equipment protection? Can you get GFCI's with different trip ratings? (I beleive the standard is 6 ma), but can you get one that trips at 9 ma and is still legal?
 

richxtlc

Senior Member
Location
Tampa Florida
Does anyone know the minimum trip rating for personal protection on a GFCI? Is there a different min. trip rating for equipment protection? Can you get GFCI's with different trip ratings? (I beleive the standard is 6 ma), but can you get one that trips at 9 ma and is still legal?

The equipment ground protection is designed to protect the equipment and not personnel. The ground fault setting depends on the size of the equipment and the circuit to which it is connected. These setting are usually high enough to kill a person.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree, Class A GFCI's trip between 4-6 ma. Older Class B GFCI's trip at a minimum of 20 ma and are not suitable for personal protection. GFPE protection used for protecting equipment will trip at 30 ma.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I agree, Class A GFCI's trip between 4-6 ma. Older Class B GFCI's trip at a minimum of 20 ma and are not suitable for personal protection. GFPE protection used for protecting equipment will trip at 30 ma.
I believe Class B GFCI's were for old pool lighting fixtures.
 

wptski

Senior Member
Location
Warren, MI
It may be 4-6ma but what's the allowable trip time? I don't have a link handy for one of those charts. You may be surprised at the lenght of the allowable trip times!
 

480sparky

Senior Member
Location
Iowegia
It may be 4-6ma but what's the allowable trip time? I don't have a link handy for one of those charts. You may be surprised at the lenght of the allowable trip times!


According to P&Ss website, the trip time is 0.025 seconds nominal.
 

wptski

Senior Member
Location
Warren, MI
According to P&Ss website, the trip time is 0.025 seconds nominal.
The current and time are like two different things. I can't find one of those current vs time curves but somebody stated 6ma at 7.2 seconds which is what I'm getting at. I tested some P&S and Leviton a while back. The Leviton's trip time was over .1 seconds.
 

480sparky

Senior Member
Location
Iowegia
The current and time are like two different things. I can't find one of those current vs time curves but somebody stated 6ma at 7.2 seconds which is what I'm getting at. I tested some P&S and Leviton a while back. The Leviton's trip time was over .1 seconds.
6ma will hold for 7.2 seconds?
Emoticon-jawdrop.gif
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The UL Standard 943 for GFCIs says this in section 6.7.1.1
The maximum permitted time to trip in seconds is equal to the quantity (20/fault current in milliamps) raised to the 1.43 power.
The application of this formula would permit a 7 second trip time for a 5 mA ground fault. Many will trip quicker, but the standard specifies the maximum permitted trip time.
 
Last edited:

wptski

Senior Member
Location
Warren, MI
One can use a Ideal Suretest 61-165 to test GFCI trip time but I used a scope which actually showed the times to be a bit faster.
 

brian john

Senior Member
Location
Leesburg, VA
The equipment ground protection is designed to protect the equipment and not personnel. The ground fault setting depends on the size of the equipment and the circuit to which it is connected. These setting are usually high enough to kill a person.

The lowest setting I have seen on a GFP relay was 1 amp minimum and 10 amp maximum, GE relay in main switchboard subfeed CB in a hospital.

They also had some 10-100 amp and then the GE standard 100-1200.

Time delays were all the same for all relays Instantaneous-1.0 seconds.

In the 25 years I have worked at this facility we have never had a trip on any of these GFP protected relays and I tested all the relays and CBs 8 times in this 25 year period.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
There is a nice chart on the second page of this document that shows the normal GFCI trip time, the maximum permitted trip time and the heart fibrillation threshold for normal adults.
 

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
090607-1525 EST

don:

The National curve is plotted on log-log and the Leviton is log-linear.

The two curves for the UL limit look to be the same by checking the mid-point and the end points.

.
 