ground faults.
im a 1st yr apprentice, so this may be a dumb question.
how does bonding and grounding a electrical system make it safer??
am i correct in saying bonding the metal surfaces together would cause a cb to trip because the combined load would draw enough current to do so, in a ground fault situation?
and what is the purpose of the ground rod??
:confused:
Welcome to the forum, and to the trade! :grin:
This forum is a great learning tool.
As an apprentice, I would presume you have a code book. Take a look at 205.4 and 250.4(A)(1 through 5).
:confused:
If your apprenticeship program does not provide it, I would strongly encourage you to pick up the latest edition of Soares book on Grounding and Bonding. It will have all your answers.
But in short, by bonding together all non-current carrying metal surfaces and raceways and such that are likely to be, or run the risk of, being energized in the event of a ground fault, you will have created an effective ground fault current path which is, like you said, designed to facilitate the operation of the overcurrent device.
Remember that electricity in a circuit always wants to go back to its source as quickly as possible. So we force it to pace itself by running it through a load. However, if a ground fault were to occur and the bonding was inadequate, there is a likelihood that exposed metal surfaces could become energized, which is a hazard because if you went and touched it and you were grounded, you could get shocked. This is why we create the effective ground fault current path, so that fault current can travel through all the bonded metal parts back to the panel, across the main bonding jumper to the neutral bus, and thus back to the power source. It creates a low impedance circuit that allows a very high current to flow (Ohm's law), thus tripping the overcurrent device quickly.
As far as ground rods, I'm not as sure about those :smile: I believe there are a couple of functions. First, in a grounded system, you have a conductor (sometimes a neutral, sometimes a phase) that is grounded. This conductor is referenced to earth via your grounding electrodes: ground rods, ufers, underground water pipe, etc. This is a subject I'm not too well versed in, so the significance of this is blurry to me. Perhaps it helps stabilize voltage. Second, it allows a quick-and-easy path for lightning to travel if it strikes the building. I'm sure there are other purposes for system grounding but I'm not entirely sure what they might be.
Perhaps someone could elucidate (or improve/correct) my statements if they are in error.
Ugh, my wife is playing the MP3 of "Funky Town" by Lips, Inc. and I can't concentrate.
Bonding conductive items together as a path from/to the electrical source enables a clear route for current to return in a short causing high amps, the high amps open the circuit. Ineffective bonding may disable high amps leaving the circuit closed (on).
:confused:
To route lightning (static) from/to earth. Without this good connection the lightning will flash multiple routes.
Welcome to the forum, you will learn alot from reading the posts.
the one who asks is a fool for 5 minutes the one who doesn't stays a fool forever.
always ask questions. no question is dumb unless it is the same question over and over and over again.
Eric
Nice job, from one apprentice to another, I think your explanation was good.
Take a peek at 250.4(A).
(A)(1) Electrical System Grounding.
This helps to understand the basics of why we ground systems.
Pay attention to "connnected to earth"
This will help you to understand the purpose of ground rods (which are only a portion of the Grounding Electrode System.
(A)(3)Bonding of Electrical Equipment.
This helps to understand why we bond non-current carrying parts.
Pau attention to "and to the electrical supply source"
Generally:
Grounding is to the earth
and
Bonding is to the source
I have to concur with the reccomendation of Soares book on grounding, it is THE number one book on the subject. Next to the code itself, should be mandatory reading for every electrician.