Customer bought a new stacked washer and dryer 220v. There existing outlet is three prong, cord on the wash/dryer four prong. So questions are: 1. Can i put a four prong outlet and put a sticker "no equipment GRD." 2. Change the cord to a three prong, and take a piece of 10awg wire and tie the GRD. and the neutral together.
 

peter d

Senior Member
Location
New England
Just change the cord on the appliance to a 3-prong and bond the neutral and ground together on the appliance if it's not done already. Don't even think of doing option #1.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I would first try and convince the owner to upgrade the wire to four conductors. If that was not the direction they wanted then I would do as Peter said--change the cord on the unit making sure the neutral and ground are bonded together.
 

celtic

Senior Member
Location
NJ
Customer bought a new stacked washer and dryer 220v. There existing outlet is three prong, cord on the wash/dryer four prong. So questions are: 1. Can i put a four prong outlet and put a sticker "no equipment GRD." 2. Change the cord to a three prong, and take a piece of 10awg wire and tie the GRD. and the neutral together.

I'd suggest you spend some time with 250.140.
 

Twoskinsoneman

Senior Member
Location
West Virginia, USA NEC: 2020
Occupation
Facility Senior Electrician
Can i put a four prong outlet and put a sticker "no equipment GRD."

This would be a violation of 406.3(B) (unless you GFCI it :D:D:D:wink:) and 250.140.

It would also be very reckless because there would be not return path for ground faults.

250.140 allows you to change the cord to 3 prong for existing circuits. Of course as was already mentioned don't don't don't forget to bond that neutral to the frame or again not fault path and dangerous.
 

JohnJ0906

Senior Member
Location
Baltimore, MD
Have you actualy taken the outlet out of the wall yet? Ive seen some 3 prong dryer outlets run in 10-3 romex, and the EGC was just pushed to the back of the box. You may be able to compliantly install the 4 prong receptacle.

Also, if the 4 wire cord is to remain, check to make sure that whoever installed it removed the neutral-to-EGC bond - it often isn't.
 

electricmanscott

Senior Member
Location
Boston, MA
Have you actualy taken the outlet out of the wall yet? Ive seen some 3 prong dryer outlets run in 10-3 romex, and the EGC was just pushed to the back of the box. You may be able to compliantly install the 4 prong receptacle.

Also, if the 4 wire cord is to remain, check to make sure that whoever installed it removed the neutral-to-EGC bond - it often isn't.


Good advice. This happened to me once. In my own house. Moved in and found three wire receptacle. changed cord to to match. Somewhere along the way I realized there was an egc doing nothing. Ten years later I changed everything to four wire. :grin:


If the appliance people installed the cord you can almost bet they left the bonding jumper and didn't use any strain releif on the cord.
 

peter d

Senior Member
Location
New England
Good advice. This happened to me once. In my own house. Moved in and found three wire receptacle. changed cord to to match. Somewhere along the way I realized there was an egc doing nothing. Ten years later I changed everything to four wire. :grin:

The old school way was to install the 10/3 in a single gang box. I even worked for a guy who did this. :roll: The 3 wire receptacles fit just fine, but the 4 wire receptacles have to be pushed in with a hammer - literally. They scrape the sides of the box.
 
Status