I am running a service out to a remote 120/240V panel. This panel will serve a number of circutis for which I have calculated the loads to be about 25kVA. I planned on running a 480V single phase circuit out to a 25kVA transformer and using a 480-120/240 stepdown transformer to feed the 100A panel.
My question is although I only have single phase loads out of the 120/240V panel would it be cheaper to run a 3-phase service? I realize that the cable would probably be smaller because of less current with a 3 phase service, but what about the cost of the transformer and panel equipment?
Since I do require both 120V and 240V loads, I would need a transformer with a center tapped delta connection and I would then have avaliable 120V, 208V (wild leg) and 240V. This would be a delta-delta transformer which may be more expensive.
In general for a case like this is it more or less expensive to run a 3-phase service?
My question is although I only have single phase loads out of the 120/240V panel would it be cheaper to run a 3-phase service? I realize that the cable would probably be smaller because of less current with a 3 phase service, but what about the cost of the transformer and panel equipment?
Since I do require both 120V and 240V loads, I would need a transformer with a center tapped delta connection and I would then have avaliable 120V, 208V (wild leg) and 240V. This would be a delta-delta transformer which may be more expensive.
In general for a case like this is it more or less expensive to run a 3-phase service?