If using breakers for switching purposes, they must be marked "SWD".
.........Circuit breakers marked ??SWD?? and rated 347 V or less are suitable for switching fluorescent lighting loads on a regular basis at their rated voltage.........
Only for fluorescent lighting.
From the UL White Book (DIVQ):
Interesting, the majority of retail spaces I have done over the years were total flouresent, all lighting switched from the panel, except maybe the sign, which was on a time clock or photocell.
Why is it you cannot use a circuit breaker to switch an incandescent light fixture?
Why is it you cannot use a circuit breaker to switch an incandescent light fixture?
Here in CA every area over 100 sq ft is required to have dual swithching and you must be able to see that area controlled by the switch.
So your local Home Depot, Lowe's, Target, Walmart have dual switch all around the store? :smile:
My point is I think there is more then what your telling us. :smile: