Site construction trailors

Status
Not open for further replies.
Construction trailers get feeders, they also are separate buildings or structures and require a grounding electrode system. See 250.32(A)
 
My take, correct me if I am wrong is if I run sevice entrance and not metal conduit I dont need sep equip ground. Just need grounding electrode at trailor.
 
My take, correct me if I am wrong is if I run service entrance and not metal conduit I dont need sep equip ground. Just need grounding electrode at trailor.

You can not run a 'service' from one building to another. Only feeders.

If you are under the 2005 or previous you may be able to take advantage of 250.32(B)(2).
 