Bus bar ampacity calculation

Status
Not open for further replies.

Mike Charron

New member
Searching high & low for a table or ruel that discribes the method of calculating bus bar ampacities. The closest I could find is article: 366.23(A). This article references ampacities as per "aux gutters"

One would surmise there must be a posted table which would allow for temperature corrections, etc...

Contacted a local switch board company in Fall River, Ma., and thet use the aformentioned reference of 1000 amps / Sg in.

What are you're thoughts??
 

drbond24

Senior Member
I went through that a couple of years ago and NEVER found an official reference. I did, however, come across the 1000 A per square inch several times from several different places as a 'rule of thumb.' From what I've seen, it is a pretty good rule.
 
Status
Not open for further replies.
Top