Can you guess where I took these pictures?:smile:
Why is photo 1 a violation? Perhaps the emt connector has a conduit attached to it.
Photo 2 has KO seals missing and the connectors don't seem to be enter straight into the box.
Regardless of the EMT if a EGC run it must be terminated properly, A hit pin used to mount the box can not be used as the means to terminate the EGC. :smile:
I assume Chris is only asking about grounding issues based on the title of this thread. :smile:
But the egc is not run in the conduit. Still illegal?
Good point, :grin: I kind of missed that.
But if that section of green was being used to ground a device we would have a problem.
As it is now in the picture the green is just extra junk in there.
Can you guess where I took these pictures?:smile:
The school?
Picture #2 does have an EGC run in the conduit, if it goes to the same panel as the
circuit that's capped off, who knows, but it should be spliced and pigtailed to the box.