I've split out 11 circuits from my 2 service panels to a subpanel fed by a hardwired 8kva UPS (double-conversion). I've found that about 2/3 of the utility outages - when testing and real - end up with a UPS failure. It maintains load for about a second and then fails hard, w/o even a message in the onboard log. The 22kw battery bank is all new and very oversized for the load, so DC voltage sag or old batteries aren't the problem. After more research I started thinking it may be due to a grounding issue. Apparently UPSs are sensitive to ground problems.
After disconnecting the subpanel feed including the ground, I got no continuity between neutral and ground so that rules out multipath neutral return due to a panel or circuit miswire/failure. But, when testing between an adjacent genset subpanel's ground and the UPS sub ground, I got continuity. So then I disconnected all the circuit grounds and tested each one individually. I found 4 of the 11 circuits had continuity. Some of the re-routed circuits didn't have enough length to be pulled directly to the sub so I ran stubs between the service panels and the subpanel; I double-checked to be sure the ground lines on all re-routed circuits do not touch any ground line or the service panel chassis. However, one of the 4 problem circuits does not double-back, it goes directly to the furnace. So I'm left with the primary ground from the 4-wire feeder, and these 4 additional grounds that somewhere, somehow feed back to ground independently. My house was built by the original owner and I've already corrected other structural and wiring issues I've found, I don't know how it passed the various inspections. It would not surprise me if he ended up bonding grounds from different circuits elsewhere in the house.
The question: before I pull my hair out trying to track down the locations of these additional ground points, should I even worry about it from a code or saftey standpoint? Anyone have any experience with UPSs and think this might be the source of my failures?
After disconnecting the subpanel feed including the ground, I got no continuity between neutral and ground so that rules out multipath neutral return due to a panel or circuit miswire/failure. But, when testing between an adjacent genset subpanel's ground and the UPS sub ground, I got continuity. So then I disconnected all the circuit grounds and tested each one individually. I found 4 of the 11 circuits had continuity. Some of the re-routed circuits didn't have enough length to be pulled directly to the sub so I ran stubs between the service panels and the subpanel; I double-checked to be sure the ground lines on all re-routed circuits do not touch any ground line or the service panel chassis. However, one of the 4 problem circuits does not double-back, it goes directly to the furnace. So I'm left with the primary ground from the 4-wire feeder, and these 4 additional grounds that somewhere, somehow feed back to ground independently. My house was built by the original owner and I've already corrected other structural and wiring issues I've found, I don't know how it passed the various inspections. It would not surprise me if he ended up bonding grounds from different circuits elsewhere in the house.
The question: before I pull my hair out trying to track down the locations of these additional ground points, should I even worry about it from a code or saftey standpoint? Anyone have any experience with UPSs and think this might be the source of my failures?