N nuvi660 Member Jun 14, 2009 #1 Is it legal to bond the niche of the light with #8 black thhn and use green marking tape at the ends. Thank you!
Is it legal to bond the niche of the light with #8 black thhn and use green marking tape at the ends. Thank you!
TOOL_5150 Senior Member Location bay area, ca Jun 14, 2009 #2 nuvi660 said: Is it legal to bond the niche of the light with #8 black thhn and use green marking tape at the ends. Thank you! Click to expand... No. Bare or green - no exceptions to that size wire. ~Matt
nuvi660 said: Is it legal to bond the niche of the light with #8 black thhn and use green marking tape at the ends. Thank you! Click to expand... No. Bare or green - no exceptions to that size wire. ~Matt
N nuvi660 Member Jun 14, 2009 #3 Thank you! I used bare and AHJ wants green only. NEC rules indicate that #8 solid is legal. do you agree!
Thank you! I used bare and AHJ wants green only. NEC rules indicate that #8 solid is legal. do you agree!
K kjw444 Member Location detroit, mi Jun 14, 2009 #4 The wire needs to be #8 green solid or stranded the key is it needs to be insulated and a listed potting compound must be used.
The wire needs to be #8 green solid or stranded the key is it needs to be insulated and a listed potting compound must be used.
C curt swartz Electrical Contractor - San Jose, CA Location San Jose, CA Occupation Electrical Contractor Jun 15, 2009 #6 Are we really talking about a Dry-Niche Luminiare as your subject indicates? They don?t have forming shells or deck boxes so there is no place to install a bonding jumper.
Are we really talking about a Dry-Niche Luminiare as your subject indicates? They don?t have forming shells or deck boxes so there is no place to install a bonding jumper.