This is an in-ground swimming pool. The pool panel with integral load center within, is being fed from an adjacent sub-panel, with a 2p, 30a, 220v breeaker. The contractor is not using the integral load center at all, instead he is taking the #10 from the 2p, 30a breaker and jumping the 3 motor contactors line side. I believe this is being done to avoid the
gfci breaker requirement in 2008 NEC requiring GFCI breakers on 15 & 20a breakers. So in all, everything is being fed with 1 2p, 30 breaker. What is wrong with this picture?