bundled conductor and temp calculations

Status
Not open for further replies.

rickh

Member
When calculating the derating factor for more than 3 conductors and temperature variance. Which do you calculate first for the end result?
 
Rick,
seen this sitting for awhile,I'll jump...I know no hard & fast rule..The way I was taught is ampacity 310.16,then ajustment factor of 310.15(B)(2)(a) then temp. correction factors @ bottom of table 310.16

Always worked for me..
 

Smart $

Esteemed Member
Location
Ohio
Rick,
seen this sitting for awhile,I'll jump...I know no hard & fast rule..The way I was taught is ampacity 310.16,then ajustment factor of 310.15(B)(2)(a) then temp. correction factors @ bottom of table 310.16

Always worked for me..
I'm in agreement with the others. No particular order, as both are factor based.

However, if I were told one must precede the other, I would say ambient temperature adjustment comes first because it is part of the Table.
 