if the conduit turns vertical and extends out of the ditch to a "fixed" enclosure or fitting, an expansion joint is often used (sometimes required) to compensate for ground movement. Often times the conduit without an expansion joint will "settle" and pull loose from the enclosure.
Have a look at 352.44. Your conduit could move 3 or 4 inches as the seasons change so expansion fittings would be required, although I don't how much the temperature changes 2 feet below grade.
if the conduit turns vertical and extends out of the ditch to a "fixed" enclosure or fitting, an expansion joint is often used (sometimes required) to compensate for ground movement. Often times the conduit without an expansion joint will "settle" and pull loose from the enclosure.
Carlon has what, to me, is a new product that appears to be a brother to the standard expansion joint and is designed for just such applications.
http://www.carlon.com/Master Catalog/Slip_Meter_Riser_Brochure.pdf
Carlon has what, to me, is a new product that appears to be a brother to the standard expansion joint and is designed for just such applications.
http://www.carlon.com/Master Catalog/Slip_Meter_Riser_Brochure.pdf
Not a new product. We have been using them here for 20 years on underground services. POCO requires them.
Jimbo, read 300.5(J) and see if your installation is coverd by that.
A run of 100 feet will move (expand or contract) 4" (4.06" per the table) if subjected to a 100 deg temp (swing)increase or decrease. This assumes the raceway is installed at maximum or minimum temperature. If the installation is made on a 50 degree day and the ambient is 100 deg as a high and 0 deg for a low, the run would be expected to move 2". Predicting the length of change is best done by calculation.
It'll move 4" as the temperature changes from 0 to 100 degrees regardless of the temperature during installation.
True, but you should gauge your installation length based on ambient temperature. If it's cold, extend it; ifr it's hot, shorten it.It'll move 4" as the temperature changes from 0 to 100 degrees regardless of the temperature during installation.
The 4.06" (or the adjusted 2.03") of movement is for a run in ambient air temperature. An undergroiund run is not subject to the same ambient temperature or swings. For an area with a 100? ambient air temperature swing through all four seasons, an ambient soil temperature swing at 2' BFG may only be 50? (just a WAG)....If you instal on a 50 degree day you would expect only 1/2 or 2.03" of movement.
True, but you should gauge your installation length based on ambient temperature. If it's cold, extend it; ifr it's hot, shorten it.
The 4.06" (or the adjusted 2.03") of movement is for a run in ambient air temperature. An undergroiund run is not subject to the same ambient temperature or swings. For an area with a 100? ambient air temperature swing through all four seasons, an ambient soil temperature swing at 2' BFG may only be 50? (just a WAG).