I have never delt with a 440v system before but I have recently been asked if a 460v 3ph freight elevator can run off of a 440v 3ph panel. Can this be done or will the voltage difference be a problem?
Only the equipment supplier can answer that definitively, but in general, NEMA specifications call for motors to be capable of +-10% voltage and still perform within spec. If they have other equipment powered from that 440V supply, that would be the most likely source of trouble, although most power supplies also have similar tolerances.I have never delt with a 440v system before but I have recently been asked if a 460v 3ph freight elevator can run off of a 440v 3ph panel. Can this be done or will the voltage difference be a problem?
Not according to Bob's chart. 440v is well within the 460v range. In fact, 440v is within 10% of 480.it's buck boost time!!