It's my opinion that in the scenario as described the neutrals shouldn't count as cccs.
The reason that neutrals count sometimes is when you get oversize neutral currents, due to non-linear load harmonic currents combining on a common neutral. If all the circuits have their own neutral back to the dimmer then those derating rules shouldn't apply as there is no current combining until you reach the neutral terminals in the dimmers.
Put it another way, if you can put n 20A circuits in a pipe when they are all connected back to a standard panelboard, each circuit with its own neutral, then in a dimmer driven scenario the circuits will never carry as much current and probably less as (a) the loads are mostly 1KW and (b) loads are often dimmed to less than 100%, so there is no reason why there should be any less circuits in the pipe just because there's dimmers involved.