GFI or ARC FAULT? Bedrooms in basement.
mudcat555
Mentor, Ohio (25 miles east of Cleveland)
Retired Electrician IBEW Local 38
This is the first time I've come across this situation. The customer is putting two bedrooms down in the basement. The code says all basement outlets are to be GFI protected, but it also says that all power in the bedroom has to be on an AFC. Do I put the bedroom circuits on arc fault breakers, and then use a GFI in each bedroom for one receptacle and piggy-back the remaining receptacles on the load side of the GFI? Given the over-sensivity associated with some arc-fault breakers, will a GFI on that circuit cause any nuisance tripping? What have others done in this situation?
GFCIs can be installed on AFCI circuits ....... but you don't have to. The NEC does not require GFCIs in the finished areas of a basement.
You only need GFI's in an UNFINISHED basement,,,,,,,,so your bedrooms added to a basement will require both arc faults and smoke detectors, but no GFI's. You probably should add a common area smoke detetector outside of the two rooms. They should be interconnected upstairs.
As the guys said, no GFCI's are needed here, but the way you described it is perfect when both are needed.
Perhaps this should be it's own thread but I saw this About a week or two ago ,. and it is bugging me. Has anyone seen where a GFCI rec. outlet is marked as incompatible with an AFCI protected circuit
In situations calling for both GFCI and AFCI protection, be sure the breaker is specifically listed for the dual purpose of both fault situations. Many GFCI outlets are not compatible for installation on AFCI protected branch circuits.
http://74.125.47.132/search?q=cache...ensions+GFCI+on+AFCI&cd=2&hl=en&ct=clnk&gl=us
ive wondered what makes a "finished" area
what if the walls are drywalled but the floor is left concrete or stained
what im saying is when is the area finished?
receptacles are required to be gfci protected in unfinished areas
is it considerd finished when its ...
insulated?
drywalled?
painted?
has floor covering?
when?