what is the temperature limitation of a breaker markt 60/75F?
what is the temperature limitation of a breaker markt 60/75F?
Seriously, a 60/75?C breaker means you can use either 60? or 75?C conductors. The choice is yours.
You mean I can't use a 90C conductor on a breaker....:grin:
It depends, Are you using a 90?C sized conductor or one with 90?C insulation?:grin:
It means the breaker can be used with the old style (i.e. rubber) insulation without its 'heatsink' effect overheating the conductors.Jim, I think I recall reading when a breaker is rated 60/75 that the 60 rating is to be used when the breaker is lined up alongside other breakers and that the 75 rating can only be used with breakers mounted singly.
Is there any truth to that or am I just all wet? :smile:
Could be both. :grin:Is there any truth to that or am I just all wet? :smile: