ATSman
ATSman
- Location
- San Francisco Bay Area
- Occupation
- Electrical Engineer/ Electrical Testing & Controls
I am posting this for aa associate in the switchgear manufacturing industry.
Thanks in advance for any advice.:smile:
Just a quick question to field engineers I have had contact with over the last few years:
I would like to find out what method and/or equipment you and your associates use to test current transformers to meet the requirements of NETA Acceptance Testing Specifications, Section 7.10, specifically with regard to turns ratio accuracy.
As an OEM, we are not required to perform this test, but we use a Megger TTR25 handheld turns ratio tester as a quick check of polarity and ratio. I have recently been told by a CT manufacturer that this is not a recognized test method, so if you could answer this for me (at your convenience) I would appreciate it
Tony
Thanks in advance for any advice.:smile:
Just a quick question to field engineers I have had contact with over the last few years:
I would like to find out what method and/or equipment you and your associates use to test current transformers to meet the requirements of NETA Acceptance Testing Specifications, Section 7.10, specifically with regard to turns ratio accuracy.
As an OEM, we are not required to perform this test, but we use a Megger TTR25 handheld turns ratio tester as a quick check of polarity and ratio. I have recently been told by a CT manufacturer that this is not a recognized test method, so if you could answer this for me (at your convenience) I would appreciate it
Tony