Typically the gas water heater is plumbed in using pipe, for both the gas and the water.
That would negate the need for (1)- facilitating frequent interchange; or noise/vibration.
Number (2) would also seem to be a remote reason for use of cord installation.
If the unit comes with installation instruction identifying the installation of a cord, I would say yes. If it does not have these instructions/identification, I would say no.
Are you saying that if the unit install instructions allows for install with a cord the install doesn't have to be a type indicated in 422.16(A)(1)or(2)? or 400.7 (6),(7),or (8)
Because I disagree..... On the other hand "facilitating frequent interchange" is an AHJ judgement call so it doesn't much matter.
Yes, that is what I am saying.
(I would bet though, that one would probably not see instructions for cord installation for hard piped units)
I agree.
You disagree with me? Get behind a long list of others.![]()
I can tell you that noise/vibration can be a problem. I have a gas on-demand water heater on the side my house. I first installed it outside the office and hard piped the gas, water and electricity. The noise was quite noticeable and rather annoying. I ended up having to move it, so when I remounted it I used vibration isolators and flexible connections for the gas, water and electric (FMC). It was a big improvement.Typically the gas water heater is plumbed in using pipe, for both the gas and the water. That would negate the need for (1)- facilitating frequent interchange; or noise/vibration.
I never really understood why the heck you can't just run cord to these kind of appliances. Its good enough for every other appliance in the house.
Instructions that come with an appliance, that allow an option such as cord, don't allow you to violate the NEC....
400.7 Uses Permitted.
(A) Uses. Flexible cords and cables shall be used only for
the following:
You may want to read 400.7(A)(8).
If a manufacturer does have installation instructions for permission to install a cord, there is usually a listing/labeling that has been part of the NRTL process.
With that said, I would approve an installation with a cord if the instructions permitted it.
Again, I have never seen such instructions or a cord installed unit, but I work in a small jurisdiction relative to the USA.![]()
I never really understood why the heck you can't just run cord to these kind of appliances. Its good enough for every other appliance in the house.
I never really understood why the heck you can't just run cord to these kind of appliances. Its good enough for every other appliance in the house.
I have some doubts about the rules on cords... that being said I can trust what I've been told about the deterioration of cords over time. Perhaps that's why something like a water heater can't usually have a cord... The WH could sit for many years without anyone ever looking at it.... never would see a cord falling apart.
How many people don't look behind their stove, dryer, washing machine, etc for 10 years or more?