service??
service??
?service? does this indicate the secondary of a xfmr. If so then the conductor ampacity is required to match the OCPD it is landing in. if this is the case 500?s would not be acceptable, and some manufacturers breakers do not have lugs for 600?s or require a different set of lugs. Also look at the wire bending radius, are you utilizing mechanical or compression lugs? You could utilize parallel 3/0?s just make sure you pick the correct grounded conductor size.