Electron_Sam78
Senior Member
- Location
- Palm Bay, FL
I have an RV park where there are 100amp breakers each supplying five 50 amp RV power pedestals. The conductors coming from the 100amp breakers are sized up to account for voltage drop (#2 AWG I believe) due to the long runs or they actually accounted for the amperage draw of 5 sites and didn't account for voltage drop. The 100 amp breakers are inadequate for 5 sites and can trip out when the site has 5 RVs on site utilizing the 50amp receptacles on a 97 degree day. So my question is can I up size the 100a breakers to 150a since the wire size is #2 AWG? See my calculations below:
Per Article 551, 5 50a RV sites at 9600VA each = 48000VA * .65 (demand factor per T551.73) = 31200VA / 240V = 130 Amps
Per Article 551, 5 50a RV sites at 9600VA each = 48000VA * .65 (demand factor per T551.73) = 31200VA / 240V = 130 Amps