These are all 50 amp pedestals (9600VA each per 551.73) with a 30 amp receptacle and a 20a GFCI.
Any suggestions on how to account for hot days and packed out sites? How would you know how much to increase the ampacity with so many unknowns? We do have information from other sites we can take into consideration. We have one loop that has 41 50a/30a combo pedestals that was 99 percent full on a day that was 97 degrees with a heat index of about 105. The loop kept tripping the main 400a CB after about 3 o'clock. Amp readings, after it was reset, showed around 280a on one leg and 480a on the other. It tripped an hour later so I don't know what the load was leading up to the trip but I hooked a recording meter to it today so we might know something better tomorrow or the next day. (I know, quite an imbalance! We have since gone around and balanced the load of the 30a receptacles by alternating legs in the pedestals - much more balanced today!) About 75% of the load is from single leg 30a RVs and about 20% comes from 2 leg 50a RVs. I'm not sure what it would look like with 75% 50a RVs...