PVC to rigid

Status
Not open for further replies.

aarong

Member
When going from pvc underground to rigid risers into panels on 480 volt system are the 2 lock nuts good enough to ensure the bonding of rigid pipe? KO is clean not eccen. or cocenn. I thought a bond bushing would be required because pipe run is not electrically continous from one end to other.
 

benaround

Senior Member
Location
Arizona
When going from pvc underground to rigid risers into panels on 480 volt system are the 2 lock nuts good enough to ensure the bonding of rigid pipe? KO is clean not eccen. or cocenn. I thought a bond bushing would be required because pipe run is not electrically continous from one end to other.

Check out 250.97 ex#3 you are good.