Wednesdays picture.
chris kennedy
Miami Fla.
60 yr old tool twisting electrician
I know I said I would spare you all any more school violation pictures, but I couldn't resist posting this. RTU 3 went south so I went up to see what was up. I couldn't get into the wiring compartment because the roofers had tarred and screwed it closed. Genius.
This is a 12?12?6 PVC J-box with a 2" rigid feeder and a 2" LFMC to the unit. Note the EGC has been stripped but there are no compression marks. Guess the installer couldn't fit a bonding bushing on the RMC so he walked away.
Maybe the grounding wire used to touch the rigid?
That bell wire will serve as a nice ground path. Maybe the grounding conductor should have been tied to those!
How can one install t-stat wire with high voltage cable in the PVC box. I am sure the t-stat wire does not have insulation equal to that of the branch circuit.
Turn your Codebook upside down..... think: "Does the high-voltage cable have insulation equal to or better than the stat wire?":D
School systems around here tend to hire the best electricians $7.50 an hour will get and the inspection system is not set up to look at their work.
I just started renovations in a school. The in house janitor/electrician has plenty of surprises like that for me too.
Have fun and get used to the saying:
'Boy, just when you think you've seen it all.'
Take pictures.
