I don't think that a dorm would be reguarded as a dwelling unit.Which outlets in a college dormitory need to be on an AFCI protected circuit? The student bedrooms are just bedrooms. All bathrooms and (1) kitchen are in common spaces. Thanks in advance
I mean regarded.I don't think that a dorm would be reguarded as a dwelling unit.
Perhaps not by the individual rooms, but the entire structure or a subdivision thereof may meet the defintion of a dwelling unit.I don't think that a dorm would be reguarded as a dwelling unit.
Then, another question would be about the use of TR receptacles.Perhaps not by the individual rooms, but the entire structure or a subdivision thereof may meet the defintion of a dwelling unit.
I am inclined to agree :smile:IMHO a dormitory does not meet the definition of a dwelling unit if the set up is multiple sleeping rooms with separate bathing and cooking facilities. I think the 210.60 (2008) covers receptacles in dormitories. I believe that a college dormitory would be treated the same as a hotel/ motel guestroom without permanent provisions for cooking within the guestroom.
Chris
IMHO a dormitory does not meet the definition of a dwelling unit if the set up is multiple sleeping rooms with separate bathing and cooking facilities. I think the 210.60 (2008) covers receptacles in dormitories. I believe that a college dormitory would be treated the same as a hotel/ motel guestroom without permanent provisions for cooking within the guestroom.
Chris
First off, 210.60 is in Part III Required Outlets. The AFCI requirement is under Part I General Provisions. How does the latter counter the former?
The only issue in question is whether the rooms are part of a dwelling unit. Sanitary, cooking, and living areas are commonly separate from sleeping quarters. What about when say each 4 dorm rooms in a building have a common kitchen, living , and bath facilities? Is this all that different from a 4 bedroom apartment that it would not be considered a dwelling unit?
Dwelling Unit. A single unit, providing complete and independent living facilities for one or more persons, including permanent provisions for living, sleeping, cooking, and sanitation.
The definition says a single unit providing permanent provisions for living, sleeping, cooking, and sanitation. IMHO a dorm with multiple sleeping rooms and a common kitchen and bathroom would not be a single unit.
I agree, to read it smart's way would mean an entire hospital is a dwelling uit.
In many of the new dorms there are a number of one or two occupant sleeping rooms, a bathroom or two and a living/kitchen area. There is only one door to the main corridor just like an apartment building would have. If the kitchen area has a cook top, or a built-in microwave, I don't think there is any question that the unit is a dwelling unit per the NEC rules. Now if the microwave is a plug in unit and just sits on the countertop, I am not so sure.The definition says a single unit providing permanent provisions for living, sleeping, cooking, and sanitation. IMHO a dorm with multiple sleeping rooms and a common kitchen and bathroom would not be a single unit. The difference between a dorm and a multi bedroom apartment would be that in a dorm each sleeping room has a separate individual that rents that room and shares the bathroom and kitchen with other residents.
Chris
Similar to what I was describing earlier...In many of the new dorms there are a number of one or two occupant sleeping rooms, a bathroom or two and a living/kitchen area. There is only one door to the main corridor just like an apartment building would have. If the kitchen area has a cook top, or a built-in microwave, I don't think there is any question that the unit is a dwelling unit per the NEC rules. Now if the microwave is a plug in unit and just sits on the countertop, I am not so sure.
Sanitary, cooking, and living areas are commonly separate from sleeping quarters. What about when say each 4 dorm rooms in a building have a common kitchen, living , and bath facilities? Is this all that different from a 4 bedroom apartment that it would not be considered a dwelling unit?
True, they are similar. But it is still taking an issue out of context and assuming it belongs somewhere where it is not in context.I never said that 210.60 counters 210.12. But what it does do is shows that dormitories and guest suites in hotels/motels are similar.
Is not a building a single unit? Can a building contain only one dwelling unit? Granted it can contain more than one, but the question is can it contain only one.IMHO, the key to whether or not a dorm is a dwelling unit is in the definition of dwelling unit.
The definition says a single unit providing permanent provisions for living, sleeping, cooking, and sanitation. IMHO a dorm with multiple sleeping rooms and a common kitchen and bathroom would not be a single unit. The difference between a dorm and a multi bedroom apartment would be that in a dorm each sleeping room has a separate individual that rents that room and shares the bathroom and kitchen with other residents.
Chris
Similar to what I was describing earlier...
Had these type of dorms when I went to college (so not so modern :grin
Of course we also had the more traditional dorms with all roomies sharing two bathrooms on each floor and on the first floor one fully-equipped kitchen and a large rec' room.
Dwelling.. a shelter in which people live. I have never understood the whole "provisions fo cooking " thing!!![]()
You gotta wash the dishes :grin:we didn't even have a fully equipped kitchen... what's that about? :roll:
Is not a building a single unit? Can a building contain only one dwelling unit? Granted it can contain more than one, but the question is can it contain only one.
The student bedrooms are just bedrooms. All bathrooms and (1) kitchen are in common spaces.
don_resqcapt19 said:In many of the new dorms there are a number of one or two occupant sleeping rooms, a bathroom or two and a living/kitchen area. There is only one door to the main corridor just like an apartment building would have. If the kitchen area has a cook top, or a built-in microwave, I don't think there is any question that the unit is a dwelling unit per the NEC rules.