JES2727

Senior Member
Location
NJ
I am installing a circuit for a welder. The supply voltage is 208V, single phase. The input amperage is 91. The manufacturer recommends input conductors of #6. They also recommend OCPD of 150 A. I've read article 630 and all of the recommendations comply. So I will pull in #4's rather than 6's because of the length, and protect it at 150 amps. I'll get some #6 SO cord to connect to the welder. What should the attachment plug be rated? Should it be rated for the load (91 amps), the wire ampacity ( 60 amps) or the OCPD ( 150 amps)? I intend to connect it with a 60 amp plug, but only because " that's the way we always do it..."
 

BenS

Member
Not that it is right.. but we have been using a 50 amp plug at 208 on a variety of welders successfully for as long as anyone can recall. What kind of machine is it?
 

BenS

Member
Thats a big one... why can't it just be hardwired? If not an option, go with 100amp plug minimum.
 

JES2727

Senior Member
Location
NJ
Thanks for the input BenS. The unit I'm connecting is a bit older. I've been looking in this manual: http://www.millerwelds.com/om/o318d_mil.pdf
The info in the electrical chart on page 15 is essentially the same as the info on page 17 of the manual you pointed me to. I still see 91 amps at 230V, and 105 amps at 200V. My source voltage is about 213V, so I'll split the difference and call it 98.
I still don't know how to rate the plug and receptacle.....
 

LJSMITH1

Senior Member
Location
Stratford, CT
If this welder is not intended to be portable (meaning no casters on it), then I would hardwire it to a wall mounted, fused disconnect. For the number of times it may need to move, it would be easier to remove and move the disconnect.
 