I don't think so....
The paralleled conductors in each phase, polarity, neutral, or grounded circuit conductor shall comply with all of the following:
(1) Be the same length
(2) Have the same conductor material
(3) Be the same size in circular mil area
(4) Have the same insulation type
(5) Be terminated in the same manner
I don't think a tap in one set meets 5. Intuatively, you no longer split the load evenly between the two conductors which is the intent of length, size, material etc.